Planning to use Southwire UF-B #8/3 w/#10G (which is what is most readily available in my area).
Currently there is a 2" PVC conduit that runs underground from the main panel to the garage which contains a 12/2 NM cable that goes to a 2-gang electrical box and splits into three branches (powering various lights and receptacles in the garage and adjacent living room. The circuit is protected by single pole 20 amp breaker. The conduit is roughly 12" below grade which is too shallow and crosses paths with a 3/4" conduit feeding the A/C compressor. This causes the 2" conduit to make over 360 degrees in bends (another violation), not to mention the wrong cable type for an underground installation.
In the process of installing a fence, I find that one of the post settings will interfere with the 2" conduit as it sits now. As there are numerous code violations associated with the current installation, I find this the perfect opportunity for the following:
- Demo existing 2" conduit, 12/2 cable, 20 amp breaker, 2-gang electrical box, and 3/4" A/C conduit
- Install new conduit from the panel to a type FSCC or similar electrical box (1 in, 2 out)
- From the two "out" ports of the FSCC box, switch the A/C conduit and garage conduit, eliminating the over 360 degree bend violation to the garage
- Route a new conduit to the garage away from post settings and at a depth of 18"
- Pull a new feeder to the A/C compressor and pull the #8/3 UF-B cable to the garage.
- Install a 70 amp indoor panel in the garage in place of the 2-gang box.
- Place the three existing branches in the garage onto three separate 15 amp breakers in the 70 amp panel.
- Replace the existing single pole 20 amp breaker with a 2 pole 40 amp ground fault circuit breaker to power the 70 amp panel via the #8/3 UF-B cable.
I believe this will eliminate any code violations, and allow the final fence post to be set. I see from the Southwire catalog that my desired cable has a dimension of 1.053" X 0.319" inches. Where I'm finding confusion is in Table 1 of Chapter 9. The table specifies a percentage of cross-sectional area per number of conductors AND/OR cables. What I am installing is a single cable with multiple conductors. Am I to assume that the "AND/OR" wording is meant to be understood as which ever carries the worst case? As the cable contains three conductors it may only occupy 40%, correct??
Thank you all for the input and any advice or recommendations.