residential electric range
Thanks for the quick reply. What column do I rate the wire. It's was installed in the late 70's.
I would guess the #8 AL was installed per the 75 deg col.
I don't have a '70's NEC, but before 2011 the 60deg col had a 30 ampacity, and in 2011 that changed to a 35 ampacity for the 60deg col. Neither of which would be acceptable in a 40A c/b.
No 8 AL in the '78 @ 60?C is 30 amps.