I was listening to a video by mike holt and I starting thinking. That is usually a problem for me...
Anyway I found that the National Institute for Occupational Safety and Health did studies that states the human body can have a resistance of up to 100,000 ohms but about 95% of the people tested had a resistance of 3,200 ohms.
Okay lets look at a scenario where someone is wet and there resistance is 50,000 ohms. Simple math I = V/R = 120V (assume this)/50,000 = 2.4 ma.
We know that a gfci will trip between 4-6 ma so if we come in contact with a grounded object and 120V on the load side of a GFCI will that gfci trip? I say know but I am curious if I am missing something. I am assuming anything over 4- 6 ma threshold is a sure trip also
I am a little late to this party and others might have already mentioned it but this is a really broad question. I think the proper term should be "resistivity" not "resistance". Resistivity is the resistance of "material" over a unit surface area and length (it is directly proportional to length and inversely proportional to surface area). Also, different parts of body have different resistance. I can image your bone is almost a perfect insulator while less rigid parts of your body are better conductors.
So to answer to your question: 120V of voltage and 2.4mA only result in about 0.24mW. You won't probably even feel it. In reality though, 120V will draw much more current through your body.