Hello;

I am designing a building and I have the requirements in the subject title. I am confused and need your help! The L5-30R is 120v, 30A. So this needs 1-phase 30A breaker in the panel. The L6-30R needs a 30A 2-pole breaker in the panel correct? Thanks!
 
You have it correct. The L5 is 120V and the L6 is 240V so they need single pole breaker and a dp breaker respectively
 
See if this helps

twist.gif
 
Nice.. definitely helpful. I am new and don't like to ask too many questions, and I thought I was all correct. Thanks, I love this forum..
 