Don't believe there is a limit. however if it is to be cord connected I would say within reach of a 5' cord.
 

kwired

Electron manager
Location
NE Nebraska
There is no code rule even directly over it however for an electric baseboard the receptacle cannot be directly over the heater
I must say that the electric baseboard rule isn't even in the code it is (pretty much always) a rule in the instructions and part of the listing of the heater though.
 

MasterTheNEC

CEO and President of Electrical Code Academy, Inc.
Location
McKinney, Texas
Occupation
CEO
I must say that the electric baseboard rule isn't even in the code it is (pretty much always) a rule in the instructions and part of the listing of the heater though.
Sure it is...:angel:

Informational Note: Listed baseboard heaters include instructions
that may not permit their installation below receptacle
outlets.
While not technically enforceable...it is still "IN" the code....lol

and



550.13(F)(3) Receptacle outlets shall not be installed above electric
baseboard heaters, unless provided for in the listing or
manufacturer?s instructions

Is indeed in the code....but not for dwellings....lol
 

kwired

Electron manager
Location
NE Nebraska
I must say that the electric baseboard rule isn't even in the code it is (pretty much always) a rule in the instructions and part of the listing of the heater though.

Sure it is...:angel:

Informational Note: Listed baseboard heaters include instructions
that may not permit their installation below receptacle
outlets.
While not technically enforceable...it is still "IN" the code....lol

and



550.13(F)(3) Receptacle outlets shall not be installed above electric
baseboard heaters, unless provided for in the listing or
manufacturer?s instructions

Is indeed in the code....but not for dwellings....lol
Ok smarty pants, rewrite of previous post:

I must say that the "no receptacles over a electric baseboard heater" rule is not a code requirement but is referenced by an informational note that it may be prohibited by the instructions of the heater. And you will find a majority of heaters out there have this instruction.

Is that better?

:)
 

MasterTheNEC

CEO and President of Electrical Code Academy, Inc.
Location
McKinney, Texas
Occupation
CEO
Ok smarty pants, rewrite of previous post:

I must say that the "no receptacles over a electric baseboard heater" rule is not a code requirement but is referenced by an informational note that it may be prohibited by the instructions of the heater. And you will find a majority of heaters out there have this instruction.

Is that better?

:)
lol....i could not help myself.....;).....
 
Status
Not open for further replies.
Top