Rai136926
- seattle, wa
Is there any NEC requirements to install a ground rod in electrical Manhole? In another words does electrical Manhole has to have a ground rod?
I do not think so but I am not 100% certain. Manholes are covered in 110 section V starting at 110.70 and I am very sure that a ground rod is not required and certainly not an GES. If a rod were installed it would be to bond the metal racks only and would not be tied to the EGC that pass through the enclosure. I see this done often for manholes that contain telecommunications splice cases.Is it a requirement for above 600v?
Is a manhole a structure? Probably.
Are there junction boxes, devices or outlets in the manhole? Does it have more than one branch circuit going into it?
Sounds to me as if it needs a GES. A Ufer would be OK.![]()
What would you think about a set of dead break (or load break) junctions mounted on the manhole wall? Incoming power terminates there, and is taken away by connecting outgoing cables. That is not exactly "utilization equipment" you would have in the manhole, but our company's standard details show a ground rod within the manhole.The key would be if a feeder is supplying the manhole, not just passing through. If the manhole contains powered utilization equipment it might require a GES.