I agree with you.I think a lot of us agree, but only because we don't really agree with the rule that the exception applies to. While the testing used to get the rule into the code clearly showed increased conductor temperatures on rooftops, there was no evidence of failures of existing installations. This was seen as just one more manufacturer driven code change...a change that was based on testing done by the Copper Development Association and designed to sell more copper.
So you see the Exception to 310.15(B)(3)(c) applying to remove ALL ambient adjustments demanded by Section 310.15(B)(2).....I disagree......the exception is (according to the location and NEC Style Manual) applying to item (c)...and the adder....not to remove the ambient adjustments demanded in Section 310.15(B)(2)...I don't see any analysis, just facts. That's what '14 code says.
Ahhh.......disagreeing with something and following the NEC is two things....again it's always about the manufacturers. Also it applies to AL conductors also.....guess they are in bed together also....I think a lot of us agree, but only because we don't really agree with the rule that the exception applies to. While the testing used to get the rule into the code clearly showed increased conductor temperatures on rooftops, there was no evidence of failures of existing installations. This was seen as just one more manufacturer driven code change...a change that was based on testing done by the Copper Development Association and designed to sell more copper.
This was seen as just one more manufacturer driven code change...a change that was based on testing done by the Copper Development Association and designed to sell more copper.
No, this code change sells less copper.
If any industry drove this code change, it would be the polyethlyene industry. To sell XHHW-2 over PVC and Nylon in THWN-2.
You are too late...the energy codes have already done that....but our next mission is Voltage Drop as mandatory....we just need to sell more Copper....:angel:
I disagree completely with the analysis/interpretation.So do you agree with this 2014 NEC NECA Analysis............![]()
The testing that drove the original rule was done by the copper association.Ahhh.......disagreeing with something and following the NEC is two things....again it's always about the manufacturers. Also it applies to AL conductors also.....guess they are in bed together also......in fact it was presented BY someone who is strongly in the Aluminum Camp......and less in the Copper Camp......read the ROP 6-41 and ROC 6-37 for more details.
...
Yeah...and I am sure all of the inspectors who do electrical inspections reference that in their codes.....to gain TEETH we need it in the NEC...You are too late...the energy codes have already done that.
The exception only applies to Section 310.15(B)(3)(c)...was my point, not as stated to remove the requirements of Section 310.15(B)(2).....as it states in image.The testing that drove the original rule was done by the copper association.
It was another change that was all based on testing and theory without any real world evidence of a problem.
I said I didn't like the original rule, and that I liked the exception because it lets me get rid of the original rule.
I disagree completely with the analysis/interpretation.
The wording of the exception is found in the section on conductors on rooftops. The plain English interpretation is that all that is being excepted is the temperature adder. But the wording "...conductors shall not be subject to this ampacity adjustment." leaves that subject to dispute.
I do find it unreasonable that an exception in the specific clause on rooftop wiring could be taken to imply exemption from all temperature based ampacity adjustments for this wire type regardless of where it is used.
I also find it nonsensical that the basic temperature based ampacity adjustment applies to this wire type everywhere but on a rooftop.
In short, I think that the commentary is flat out wrong.
It would have been better if the wording of the exception specifically referenced the temperature adder and not the "ampacity adjustment".
PS: Just like the Handbook, the Analysis of Change does not have the normative standing of the Code itself. And in this case I think they blew it.
Yeah...and I am sure all of the inspectors who do electrical inspections reference that in their codes.....to gain TEETH we need it in the NEC........we will use those ASHRAE and Green Code and others to give teeth to the proposal...look out 2020.
Only you would read it that way...........I will be nice.....I don't know if you are joking or not.
If you are serious I find it very disturbing and a conformation of using the code to make sales.
I don't see how an energy use rule would be within the purpose of the NEC.Yeah...and I am sure all of the inspectors who do electrical inspections reference that in their codes.....to gain TEETH we need it in the NEC........we will use those ASHRAE and Green Code and others to give teeth to the proposal...look out 2020.
I looked right over the wording, both when read this post and when I taught the changes using that book.The exception only applies to Section 310.15(B)(3)(c)...was my point, not as stated to remove the requirements of Section 310.15(B)(2).....as it states in image.
Only you would read it that way.
..........I will be nice.....
But I happen to believe Voltage Drop is important.....so if I did support it the reason would be for the merit of the intent.
No, I doubt that I am the only one that reads it like that. You work for a manufacturer to shape the code for the benefit of the manufacturer. You are not being put on a CMP for the benefit of society.
Be whatever you want, I am a big boy.
It is important but it is a design issue not a safety issue.