Carultch
- Massachusetts
I understand that parallel feeder sets have to be routed under conditions that would give each set an identical resistance. Same length, same conditions of use, same conduit, same terminations, etc. 310.10(H).
I have a situation where I have two parallel 4" conduits to work with, and I have to tap 800A of wire onto a 3-set single phase 1200A feeder. They penetrate a substantial wall, which I'd rather not add in another penetration.
One potential solution is to use 3 sets of 300 kcmil, and send two sets in one of the conduits, with the remaining set in the third. Like I said, conduits are less than 24", so the following would ordinarily apply in any other situation: 310.15(B)(2)(a) Exception No. 3: Derating factors shall not apply to conductors in nipples having a length not exceeding 600 mm (24 in.)
Sets 1 and 2 in the first conduit still have the same ampacity adjustment factor due to bundling as set 3 in the second conduit. I.e. no ampacity adjustment, due to the length. But it doesn't exactly "feel right".
Other solutions:
1. Isolated "phase" installation. Black phase in pipe 1, red phase in pipe 2. Distribute the non-current-carrying neutral however it may fit, and a ground in each. It is PVC conduit.
1. 8-terminal tap connectors, for 3 wires in / 3 wires out / 2 wires tapped.
Other solutions: