I came across an issue where I was getting 99volts on the switched receptical and 120 on the constant part of the receptical.
The rest of the outlets down the branch circuit line were 99volts also....
So I opened up the switched outlet. I discovered that in addition to the brass tab being removed the silver grounded tab was removed. (no pigtails obviously)
I replaced with a new receptical and removed just the brass tab. The issue was fixed.
Could it be that the other outlets that I had 120 volts on the switched and constant part were detabbed incorrectly also. :? Would the missing neutral tab explain the 15 volts on the dead switched portion?