Above Ground Pool Bonding
A temporary service is installed to supply receptacles for an above ground swimming pool. Should the equipotential grid installed around the pool be bonded at the service disconnect?
The equipotential bond is present to perform the task associated with it's name. It is not a "grounding" means even though it becomes grounded thru bonded equipment. There is no reason to connect it to the service equipment.
Is there an article in 250 or 680 that I could reference for not making the connection at the service? Also, do you have a recommendation on how to bond the water?
Look here:
680.26 Equipotential Bonding.
(A) Performance. The equipotential bonding required by
this section shall be installed to reduce voltage gradients in
the pool area.
(B) Bonded Parts. The parts specified in 680.26(B)(1)
through (B)(7) shall be bonded together using solid cop-
per conductors, insulated covered, or bare, not smaller than
8 AWG or with rigid metal conduit of brass or other iden-
tified corrosion-resistant metal. Connections to bonded
parts shall be made in accordance with 250.8.An 8AWG or
larger solid copper bonding conductor provided to reduce
voltage gradients in the pool area shall not be required to be
extended or attached to remote panelboards, service equip-
ment, or electrodes.