Topherball
- La Mirada, CA, USA
Electrical System infrastructure:
1) We have two 2000 kVA transformers that feed our campus 5kV underground distribution system they are redundant and each can handle the full campus.
2) We have three- 5 switch Sectionalizing Switches to distribute out to our buildings.
3) Both transformers and all lines are phased properly so we can either be in loop config or radial with one transformer taking care of two of the Sectionalizing Switches, and the 2nd one taking care of the other switch.
I have been running the system in a radial configuration, not a loop configuration. My thinking is if we lose something we do not lose the whole campus. I am now being asked why this is better than having a loop configuration with each transformer feeding from each end.
Is there a "best practices" application for this? I guess if each is sharing the load both transformers would run cooler, and if there was a failure of either transformer or on the feed to either transformer, and a fuse blows, the other transformer would then be able to handle the campus. Your thoughts?