Burned up metal halide ballast

Status
Not open for further replies.
See if this helps. Just use 480/277V instead

ry%3D400
 
Last edited:
My understanding, and I might be wrong, is that over voltage drives the ballast core onto saturation. When saturated there is not enough counter EMF to limit current on the windings and thus the windings will begin to have more current flow. The current flow heats the coils until they overheat.


Am I correct? I am curious about this as well.
 
My understanding, and I might be wrong, is that over voltage drives the ballast core onto saturation. When saturated there is not enough counter EMF to limit current on the windings and thus the windings will begin to have more current flow. The current flow heats the coils until they overheat.


Am I correct? I am curious about this as well.

Yes. The normal current flow is limited by the circuit which consists of a relatively fixed voltage drop across the lamp and the remaining voltage being dropped by the inductive impedance of the ballast coil. Once the ballast is driven into saturation, the current required for a given voltage drop (more than double the normal voltage drop) will be far higher than just twice the normal current.
Note that unless the ballast also contains an autotransformer or isolation transformer circuit, the entire excess load current will also pass through the bulb, and may damage it too. It is a question of which fails first.
 