During a loss of one phase incident this week I noticed a 230V single phase refrigeration machine trying to self destruct.
I opened the line disconnect and found 120V potential [not ghost voltage] and the main contactor coil seeing that power with the typical results.
Some background on this type of effect by my experience.
What I have seen and dealt with in similar situations sometimes involves a neutral downstream that the 230v circuit interacts with which can cause this kind of thing to happen. An example would be on a 230V single phase refrigeration condenser with 120V Fan bank. Its common and typical to feed the Liquid Line Solenoid at the Fancoil unit from the N.C. contact [4] on the condensing unit defrost timer. Often times the solenoid coil is 115v because the fancoil unit is also 115v and they are set up that way. I have had to wire more complex control schemes such as nonrecycling pumpdown which require extra 230V coil relays in the condensing unit cabinet which do not like to interact with a 115V LLSV. Do away with the neutral and change the LLSV to 230V coil and the problem goes away. You will no longer get strange feedbacks that give you a partial voltage to a relay coil that could burn it.
This is just one example.
SO I am getting through the power phase loss and next day I have another piece of gear with a smoked contactor coil which I did not catch during the outage. Its a 3phase ice machine remote condenser, so the main contactor control coil is 230V.
ON a per equipment basis it could come of as time consuming to sort out.
I have maybe 3 units remaining that I will have to address that are single phase which could be a problem.
I am interested in any other experience and solutions for this type of scenario.
Warren
I opened the line disconnect and found 120V potential [not ghost voltage] and the main contactor coil seeing that power with the typical results.
Some background on this type of effect by my experience.
What I have seen and dealt with in similar situations sometimes involves a neutral downstream that the 230v circuit interacts with which can cause this kind of thing to happen. An example would be on a 230V single phase refrigeration condenser with 120V Fan bank. Its common and typical to feed the Liquid Line Solenoid at the Fancoil unit from the N.C. contact [4] on the condensing unit defrost timer. Often times the solenoid coil is 115v because the fancoil unit is also 115v and they are set up that way. I have had to wire more complex control schemes such as nonrecycling pumpdown which require extra 230V coil relays in the condensing unit cabinet which do not like to interact with a 115V LLSV. Do away with the neutral and change the LLSV to 230V coil and the problem goes away. You will no longer get strange feedbacks that give you a partial voltage to a relay coil that could burn it.
This is just one example.
SO I am getting through the power phase loss and next day I have another piece of gear with a smoked contactor coil which I did not catch during the outage. Its a 3phase ice machine remote condenser, so the main contactor control coil is 230V.
ON a per equipment basis it could come of as time consuming to sort out.
I have maybe 3 units remaining that I will have to address that are single phase which could be a problem.
I am interested in any other experience and solutions for this type of scenario.