The engineer purchased a 3 phase 45kva transformer with the idea it can be used for future expansion if needed. Problem is he did not get a distribution panel-board. So it is going to feed a 100 amp panel only at this time. If this transformer is properly sized for it's capacity then the secondary conductors will not physically fit in the 100 amp lugs! This is primary protected only. So the question is would it be acceptable to use an undersized breaker (calls for a 70 amp) on the primary so a smaller conductor can be used for the 100 amp panel. Then document that the secondary will need upgraded if it ever becomes necessary to expand. The primary conductors are already installed for the 70 amp protection. This is an industrial installation and I was asked what can be done after they pulled in the conductors and realized the problem. Thanks