I am installing a 20KW generator in a NON DWELLING application. There is an existing 200 amp main distribution panel and a 100 amp sub panel. I will be selecting various circuits from each panel and have installed a 3/4" EMT conduit from each panel to the transfer switch (with load center). I have seen many installations of transfer switches wired without neutrals brought over. I have also noticed that the Reliance brand and other manual transfer switches only carry one neutral and one ground wire to them.
The main panel has just a neutral bar and of course, the sub panel has a neutral bar and a ground bar. The transfer switch has both a neutral bar and a ground bar.
Can I bring over all the hot wires and just one neutral and ground wire to alleviate overheating in the ferrous 3/4" conduit? (300.20)
I'm not sure that will be OK since there will not be current in the neutral wire.
It seems redundant to bring over all the neutrals and grounding conductors, since they are already landed properly in the existing panels.
Also, how are the grounding conductors handled when some are landed on the neutral (main) and some on the ground bar (sub) going to one transfer switch?
It is a church basement, so I did not want to use PVC.
The main panel has just a neutral bar and of course, the sub panel has a neutral bar and a ground bar. The transfer switch has both a neutral bar and a ground bar.
Can I bring over all the hot wires and just one neutral and ground wire to alleviate overheating in the ferrous 3/4" conduit? (300.20)
I'm not sure that will be OK since there will not be current in the neutral wire.
It seems redundant to bring over all the neutrals and grounding conductors, since they are already landed properly in the existing panels.
Also, how are the grounding conductors handled when some are landed on the neutral (main) and some on the ground bar (sub) going to one transfer switch?
It is a church basement, so I did not want to use PVC.