I have a confusing service entrance scenario that I really need a second opinion on...
we have an existing 1600A service entrance panel, a ~10' wireway, and a 1600A MDP.
The 10' wireway has what looks like three triplexed sets of 500kcmil conductors, 4 parallel 500kcmil non-triplexed neutral conductors, and what looks like a 500kcmil ground if the wireway is not rated for or used as one.
Temperature derating does not apply, number of conductor derating does not apply (under 30, wireway). I am using the table for this 'raceway' as wireway is defined as, 310.15(B)(16).
I am assuming this is 75C, rather than 90C. It seems like these conductors are undersized. Does anyone know of any way that the original engineer could have installed like this? Even if I miscounted 4 sets would not be enough. It can't be a delta because the GFCI at the service wouldn't work. 240.4(B) can't apply, over 800A and also a tap. I'm stumped. Only thing I can think of is that it was designed as a cable tray and installed as wireway.
any help is appreciated.
we have an existing 1600A service entrance panel, a ~10' wireway, and a 1600A MDP.
The 10' wireway has what looks like three triplexed sets of 500kcmil conductors, 4 parallel 500kcmil non-triplexed neutral conductors, and what looks like a 500kcmil ground if the wireway is not rated for or used as one.
Temperature derating does not apply, number of conductor derating does not apply (under 30, wireway). I am using the table for this 'raceway' as wireway is defined as, 310.15(B)(16).
I am assuming this is 75C, rather than 90C. It seems like these conductors are undersized. Does anyone know of any way that the original engineer could have installed like this? Even if I miscounted 4 sets would not be enough. It can't be a delta because the GFCI at the service wouldn't work. 240.4(B) can't apply, over 800A and also a tap. I'm stumped. Only thing I can think of is that it was designed as a cable tray and installed as wireway.
any help is appreciated.