2011 NEC section 334.12(B)(4) does not allow the use of these cables in in wet or damp locations. I have a contractor that says it would be compliant if it is installed in conduit. I don't see any exceptions to this section. Any thoughts? :huh:
 

construct

Senior Member
Where in the code does it say that something inside a wall is in a damp location?

It doesn't that I'm aware of. The closest I've seen to this is 300.5(B) that considers the interior of enclosures or raceways installed underground to be a wet location. That's why I was interested in the opinions of others.
 

construct

Senior Member
I agree "iwire", they would have bigger problems. My opinion is the same as all of the replies. Not a wet or damp location. Just wanted some feedback from others.

Thank you all for the responses. :happyyes:
 