Parallel conductors
Badgerstate
Wisconsin
Can I install all phase conductors and neutral conductors in separate raceways? all phase A in one conduit, all phase B in one concduit, ect. ect.?
Read the exception to 300.3(B)(1) and then read 300.20(B)
Roger
In a parallel installation you should have each phase and the neutral in each pipe. It is necessary to cancel out the inductance created between the conductors.
I take it you didn't read the code sections I posted.
Roger
The topic you are looking for is isolated phase installations. They are permitted, but there are a lot of conditions that affect how you do it. The main condition is that you cannot use ferrous raceway components of any kind, including steel locknuts on PVC male adapters.
For best results, each conduit should contain a full set of conductors, all phases, neutral, and EGC.