Bonding and Grounding on funky trough service at late 1700's build home
ShauwnC
Fairfax virginia
The service after we upgrade will be as follows. A 400A fused switch ( existing to remain ) Feeding a 8" x 8" x 48" wireway. From the trough two 200A main breaker panels will be fed( one with a 200A service rated transfer switch before the panel it feeds) . The main question I have is since there are parallel 4/0 thhn cables per phase and the disconnect is old an has no current neutral block, Am I correctly grounding and bonding the new setup. I am running 1/0 GEC to the primary electrode which stops at the disconnect isolated neutral busbar ( installing since there isn't one in the existing disconnect ). The ground rods will have #6 to the same busbar and that busbar will be bonded to the enclosure. From the neutral plate/busbar I will run the neutral to a tap in the trough as well as the two ungrounded phase conductors which will also be tapped to serve the two panels. From the Neutral plate/bus bar I will run a # 3 cu based upon 250.122 to a lug in the trough. The neutrals and grounds will of course be separated in my panels and a #4 from each panel will go through the trough without terminating in the trough and then terminate on the neutral busbar in the disconnect. I am attaching a riser diagram ( not my best or cleanest diagram ) aand want to know if my install is correct primarily bonding and grounding related.
0
1st let me suggest that you simply run one set of your 4/0s (oversized) to each of the disconnects.
There is no need to "parallel" them as long as you comply with the 240.21 tap rules.
Beyond that, a qualifying metal raceway could service as your grounding conductor to the raceway and the switches but if you wish to install a grounding conductor it should be sized as a #3 to each disconnect since the protection is the 400 amp fuse.
Your grounding electrode conductor plan looks fine.
You did not indicate, but how is the 400 amp being fed ? Do the service wires come thru your wireway.
This is the funky part. The 400A disconnect is technically utility incoming but this home was built in the late 1700's and the meter is a pole mount CT meter on the pole approx. 200' away. The really funky part is the A phase is two 4/0 cables, the B phase is two 4/0 cables and the neutral is one 4/0 cable all in one 3" RMC. Load side is also paralleled off the disconnect so since I will be utilizing the 25' tap rule to feed the ATS and then on to the gen panel, I might as well have taps in the trough. I was considering using PVC from disco to trough and on to panels to eliminate bond bushings as well. Here is a picture of the existing setup.
0
0
That smaller neutral may seem funky but code says it can be as little as a single 1/0 conductor if you can show calculations that it will not have any more load then the 1/0 can carry. That is for the portion that is service conductors, for a 400 amp feeder it can be as little as a single 3 AWG if the neutral load is less then what a #3 can carry.
If you have a lot of straight 240 volt load this makes it easier to consider such a reduction of neutral size. The more 120 volt load you have the harder it is to determine what the maximum neutral current may be at any point in time.