Hi there!
I need help to size a transformer that will be used in a supermarket.
According to my calculations, I get the following kVA:
To get these numbers I start measuring Amps for each item. The formulas are shown below:
kVA(1-Phase) = Volts * Amps / 1000
kVA(3-Phase) = Volts * Amps * sqrt(3) / 1000
where Volts: 220V (S. America)
The total Power is 552kVA. So I added an extra 20% and I get 663kVA.
What size of transformer do you recommend? Is it better to have 2 transformers with lower capacity or a big one? Will compressors in the system have to be considered for power correction? Thanks in advance for your support!
Details on Power Calculation:
| Item | Qty | Power/unit | Power | 1-Phase | 3-Phase |
| Microwave | 1 | 12A | 12A | 2.64kVA | |
| Fan | 1 | 0.5A | 0.5A | 0.11kVA | |
| Ventilation | 1 | 2A | 2A | 0.88kVA | |
| Scale Type1 | 4 | 0.3A | 1.2A | 0.264kVA | |
| Scale Type2 | 1 | 1.5A | 1.5A | 0.33kVA | |
| Hydraulic Press | 1 | 4A | 4A | 0.88kVA | |
| PC | 1 | 1A | 1A | 0.22kVA | |
| Kitchen Cutter | 1 | 3.5A | 3.5A | 0.77kVA | |
| Scale Type3 | 1 | 0.3A | 0.3A | 0.066kVA | |
| Packager | 3 | 1.5A | 4.5A | 0.99kVA | |
| Meat Grinder | 1 | 2.5A | 2.5A | 0.953kVA | |
| Meat Saw | 1 | 1.7A | 1.7A | 0.648kVA | |
| Vacuum Packager | 1 | 7.5A | 7.5A | 1.65kVA | |
| Checkouts | 18 | 5A | 90A | 19.8kVA | |
| Server | 1 | 5A | 5A | 1.1kVA | |
| Cooling Equipment | 1 | 400A | 400A | 152.4kVA | |
| Water Pump 1 | 1 | 4A | 4A | 1.52kVA | |
| Water Pump 2 | 1 | 5A | 5A | 1.9kVA | |
| Illumination | 1 | 214.4A | 214.4A | 94.33kVA | |
| AC Unit 360k BTU | 5 | 51.4A | 257A | 97.93kVA | |
| AC Unit 500k BTU | 1 | 71.4A | 71.4A | 27.2kVA | |
| AC Unit 18k BTU | 1 | 9.1A | 2A | ||
| Electrical Doors | 2 | 0.8A | 1.6A | 0.35kVA | |
| Kitchen Equip 1Ph | 1 | 11.85A | 11.85A | 5.2KVA | |
| Kitchen Equip 3Ph | 1 | 362.7A | 362.7A | 138.2kVA | |
| SUB TOTAL | 131.74KVA | 420.78kVA | |||
| TOTAL | 552.5kVA |