Two VFDs fed off single breaker
LMAO
Texas
Two identical VFD breakers fed off identical conductors protected by a single breaker...? There shouldn't be an issue as long as conductors are sized appropriately with respect to the main breaker, correct?
/------------breaker------------VFD------------motor
main breaker
\------------breaker------------VFD------------motor
Cow
Eastern Oregon
I don't see an issue, but I'd also make sure the breaker hasn't been oversized beyond the manufacturers recommended breaker size for the drives.
EDIT: I didn't notice the individual OCPD in line with each VFD, so disregard my post. You should be fine.