240 sq.mm
Not sure of the exact ampacity of 250 sq.mm conductor but it is roughly equal to a 350 mcm conductor. 350 al is rated 250 amps at 75C and 280 @ 90C
500 mcm is rated 310 at 75C or 350 at 90C
Question,
What is ampacitiy of 240 sq.mm as compared to 500 mcm XHHN 2
Depends on a number of factors. Single core, in free air, embedded in a wall...........
Anywhere from about 400A to 600A according to BS 7671.........
Wondering this myself...???
AFAIK, there are no mm²-sized conductors which are a type recognized by the NEC.
that would be the real issue.
I think there are some these days, but I can't recall the last time I ran across them, and I seem to recall only seeing them in smaller sizes.
I know some DLO cable is listed as RHH/RHW, what to do as far as crossing it with a standard AWG size (above 4/0) is a different matter.
Roger
it is not all that hard to convert from mm^2 to kcm. They are just two different units of cross sectional area.
However, most conductors spec'd in mm^2 are not of a type that the NEC recognizes, as has been mentioned in previous posts, so even if you can come to some kind of conclusion about its ampacity, if it is not a NEC recognized type of conductor insulation, you can't use it in a NEC installation.
Roger
I thought all of the larger DLO was in circular mils...just some non-standard ones like 262.6, 313.3 and 535.3 kcmil (there are others too). I just use the next smaller standard size for ampacities where I am using DLO. You do have to watch out for the manufacturer's ampacities for DLO...they are almost always based on 90° C in free air.
That was actually my point Don, up to 4/0 they are sized the same as AWG, after that the larger sizes are in circular mils. We do the same as you do when we do use it but I guess it could be questioned by someone.
Roger