Class 2 wiring method for lighting

Status
Not open for further replies.
I'm installing several low voltage recessed LED lights that have remote mounted Hi-Lume Lutron drivers. I am having a difficult time trying to find the proper stranded conductor to run between the driver and the fixture. Would I be correct in assuming that if I use a in-wall rated class 2 (150v) or a in-wall class 3 (300v) speaker wire for these fixtures it would be done as per the code?
 
My 2017 code change for TC cable addressed this application in which the committee stated "the proposed language does not add any addtional information" so my conclusion is that no change was needed to use TC cable is this application.
 
The particular speaker wire you have presented will not be in the table of article 400 -- Is rated as a CL3 see Figure 725.154(A)
 
I'm installing several low voltage recessed LED lights that have remote mounted Hi-Lume Lutron drivers. I am having a difficult time trying to find the proper stranded conductor to run between the driver and the fixture. Would I be correct in assuming that if I use a in-wall rated class 2 (150v) or a in-wall class 3 (300v) speaker wire for these fixtures it would be done as per the code?
Have you considered installing the newer Type MC-PCS products that incorporate the Class 2 conductors and normal power conductors in a common Metal-Clad Cable?

I guess if you are not using Type MC in this project it would be a pain to do so.....but just in case.
 
That type of wire is for 0-10v dimming only. The lights I'm using are forward phase Lutron high lume drivers. I need to get my secondary conductors from the remote mount drivers to the LED drivers.
 
Would I be correct in assuming that if I use a in-wall rated class 2 (150v) or a in-wall class 3 (300v) speaker wire...
It's fine. Any cable listed CL2 or CL3 can be run within structures (but not plenum or riser). Further, just because somebody is calling it "speaker wire" means nothing- except that you are probably getting ripped off on cost. Go ahead and use it but consider that there is other 14/2 CL2 wire out there that is probably cheaper. -Hal
 