- Windsor, CO NEC: 2023
- Hospital Master Electrician
You don't typically have high leg to neutral loads on a 4 wire delta system. The line to neutral loads are across a single transformer winding, exactly like they are on a single phase center tapped transformer. The two lines across the center tapped winding of the 4 wire delta system are on the opposite ends of a single sine wave (often called 180° our of phase) and the neutral load cancels just like on a single phase system.
I still don't get it. If I hookup a three phase load to a delta system, it behaves as a three phase load because it's a three phase source. If the B phase is part of the source, electrons will want to seek it, otherwise three phase loads would single phase. So why isn't some current on your single phase loads looking for B as much as A and C?
High leg is irrelevant; it doesn't matter which phases I use of a wye, the neutral current will equal the lines when they are equal to each other. Grow the b-phase away from the neutral point (increasing the voltage of that phase), why would it matter to the neutral current? It's still fighting to get to the third phase it doesn't have ready access to.
What am I missing?