According to the optional method for dwelling units (220.82), there are only a couple of load types that everything gets categorized into:
HVAC: 65% of heat + 100% of fan/compressor etc.
General Loads: First 10 kVA @ 100% + 40% of ALL other loads.
In the case where you have shore power for a large boat, with a shore power panel equipped with a 50A, 240v receptacle, would it be permissible to categorize this into the "General Loads" category? I dont see why this wouldn't be acceptable but I have a local plans examiner/inspector that thinks otherwise.
Alternatively this load of 12 kW would be added directly on to the service as he claims is required. My problem with this is that this chapter is labled "Marinas & Boatyards". In fact, in 555.1, it actually says "Private, noncommercial docking facilities....are not covered by this article".
All references are to the NEC 2011.
Thanks.