Ceiling fan
mepengineer
New York, NY
View attachment 13297Thought i had a Juntiin box to mount my ceiling fan.. Now is a project. I am thinking of just plugging the fan to a receptacle. The fan has a Black.. White.. Blue..
I have some #12 Black.. White and Green. Which i want to connect to the can and extended to a replacement cord whic is going to the receptacle.. Any help
Sent from my SM-G900T using Tapatalk
1.The green is the ground and is in the hardware thats goes on the ceiling..
3. Yes they both have pull chain
4. Dont know the rating.
Good.
Good.
Code requires a fan rated box or fan has to be independently supported.
314.27
(C) Boxes at Ceiling-Suspended (Paddle) Fan Outlets.
Outlet boxes or outlet box systems used as the sole support of
a ceiling-suspended (paddle) fan shall be listed, shall be
marked by their manufacturer as suitable for this purpose, and
shall not support ceiling-suspended (paddle) fans that weigh
more than 32 kg (70 lb). For outlet boxes or outlet box systems
designed to support ceiling-suspended (paddle) fans that
weigh more than 16 kg (35 lb), the required marking shall
include the maximum weight to be supported.
Good.
Good.
I dont have a junction box to mount it.. I will drill it to the ceiling..
Now in the 3 prong cord... I guess the black on it withe the black/blue on the fan.. The white on the fan to the other on the cord(no color noted) and the middle on to the ground...
Where can i ground thr ground wire.. I have no junction box?
I am sorry but this really getting DIY. I have probably already let it go too far.
I doubt that the fan is listed for a cord connection.
At this point I gotta recommend you hire an electrician.