If the rebar is coated I can not use it . must I run a 20' of #4 bare copper ? or can I use a ground rod ?
If I build a new home must I use a 20' rebar as a grounding electrode if available ?
Although in some cases, such as rocky or dry sand soil you might want be sure that a Ufer is made when the concrete is poured, even if it means adding a non-structural length of rebar for that purpose.The CEE is present and must be used only if it's 20' or more of 1/2" or larger non-coated rebar. There is no requirement to make one if it doesn't exist.
In every case I would say.Although in some cases, such as rocky or dry sand soil you might want be sure that a Ufer is made when the concrete is poured,.....
If I build a new home must I use a 20' rebar as a grounding electrode if available ?
Translate CEE for me?The CEE is present and must be used only if it's 20' or more of 1/2" or larger non-coated rebar.
Translate CEE for me?
Thanks.Concrete Encased Electrode.