OK OK, perhaps I am just being obtuse. I run service conductors from the outdoor transformer to a switchgear inside the building. The N-G bond is inside the switchgear. The service conductors are four sets of 500 MCM copper. I put a ground bar on the wall next to the switchgear. I put two ground rods outside the building. Table 250.66 tells me the wire from the switchgear's internal ground bus to the ground bar on the wall needs to be 3/0 copper. But does 250.66(A) allow me to use only a #6 copper from the ground bar on the wall to the ground rods outside the building? And if I run from the ground bar on the wall to the water service pipe, am I back to a 3/0?