Raventai
- Alachua Florida
I maintain a mid sized factory here in Florida, we have two mail electric suplies from the electric utility, 3 phase 480/277 and the other 3 phase 208/120, we have no native 240V supply.
this has been a bit of a problem with contractors equipment, especially now as we are doing a renovation, some 240v tools will run on the 208, some contractors not comfortable hooking their equipment to it. and I don't not have 208 handy in many places, it is generally distributed as 120v oultets. for instance today I have floor grinders here polishing the floor, the closest 208 pannel is 200' from where they are working,
What do I have throughout the facility is 60 amp 3 phase 480 volt outlets for our welders.
I also have a 75 KVA 3 phase transformer, 3p 480v to 3p 240, Square D style 3439-28212-016
what I would like to do is bolt this transformer to a pallet with a cord and the same 480v plug as our welders and feed the 240v output to a breaker box also mounted on the pallet with 240v outlets, what i envision is being able to fork this thing to where contractors are working and provide 240v outlets they can plug into, the 60 amp of our welder outlets is a bit small to fully power the transformer (90 amp input for 180 amps output) but I should still be able to get 100-120 amps out with 60 in. my plan is to set this up and then have our electrical contractor look it over before use,
problem is I am not sure how well this transformer will like the unbalanced load of picking off one phase, if i have 3 identical tools running I may get some balance, but that would be rare, would that be a problem? what else should I look out for?