david
- Pennsylvania
I am having a tense disagreement with a PV contractor, 230.2, 690.56, 705.10
I am asking for signage at the normal service disconnect location.
(NFPA 70 / 705.10 Directory.
A permanent plaque or directory, denoting all electric power sources on or in the premises, shall be installed at each service equipment location and at locations of all electric power production sources capable of being interconnected.)
In support of that request I also made note of 690.56 and 230.2 for consideration.
The only reference the PV contractor is willing to reference is 690.56 based on 690.3 “other articles”.
His position is this since the Utility company requires signage at the meter location and he must comply with their requirement before the utility will allow inter connection with their utility he has complied with 690.56 since 690.56 does not state that the signage has to be at the normal service disconnecting means.
Hs second very blunt statement is that 705.10 is different than 690.56 and he quotes “wherever the requirements of other articles of this Code and Article 690 differ, the requirements of Article 690 shall apply “ based on 690.3
This is a line side interconnection point at the meter location and (he) is insisting that I am trying to define the PV equipment as service equipment otherwise I have no right to require anything at the existing service disconnecting location, since what he installed is PV equipment and has nothing to do with the existing utility service.
I want signage at the normal service disconnect location in the basement of this dwelling.
I agree that 690.56 does not indicate in its language the location of the signage. I also agree that the utility company requires signage at their meter location. I disagree that because 690.56 does not designate a location that I as the authority or one representing the authorities interest cannot designate where the authority wants the signage.
I see no conflict between 690.56 and 705.10 even though the details are different in both sections in that 705.10 is more specific in designating the location of that signage requirement. Of course his position is 690.3 doesn’t say the sections have to be in conflict it’s just says if the requirements are different.
Thirdly I disagree that when you “tap” the load side of a meter enclosure in this case change out the existing meter to provide one sized to double lug the load side, that you are not touching the existing service.
I do not believe that I am trying to define the PV equipment as a service disconnect because a am asking for signage at the existing service disconnect as if the requirement was based on 230.2 or part IV of article 230.