Hello…
I picked up a generator last year figured I'd get it set up to plug in in case of a outage..
It's small with the inverter, Honda eu2000i. (single phase, 120v)
The specs show that it's ground is "floating".
If I take a multi meter reading from neutral to ground I get 60v.
It reminds me of a clean balanced power unit I have where they tap the center of the winding to create a ground and H to N is 120v and N to G is 60v … (I screwed up and didn't check H to G, but figure it would be 120, 60 or 0
)
I remember finding literature in one place and only one place last year when I was researching this unit that showed this configuration.
All the research I've been doing now shows only a floating neutral.. Two honda techs also say the neutral floats..
I'm considering removing the panel neutral wire when the generator is running as I don't want to send 60v on the neutral. I'm also curious what will happen to the neutral/ground of the generator if I bond it at the unit, or let it bond at the electric service bond.
I found this post and it mentions the voltage reading N to G is not a true voltage.
Should I disconnect all leggs at the panel, just disconnect hots and leave neutral and ground bonded?
attached, post and clean power, and honda sch.
Thank you
I picked up a generator last year figured I'd get it set up to plug in in case of a outage..
It's small with the inverter, Honda eu2000i. (single phase, 120v)
The specs show that it's ground is "floating".
If I take a multi meter reading from neutral to ground I get 60v.
It reminds me of a clean balanced power unit I have where they tap the center of the winding to create a ground and H to N is 120v and N to G is 60v … (I screwed up and didn't check H to G, but figure it would be 120, 60 or 0
I remember finding literature in one place and only one place last year when I was researching this unit that showed this configuration.
All the research I've been doing now shows only a floating neutral.. Two honda techs also say the neutral floats..
I'm considering removing the panel neutral wire when the generator is running as I don't want to send 60v on the neutral. I'm also curious what will happen to the neutral/ground of the generator if I bond it at the unit, or let it bond at the electric service bond.
I found this post and it mentions the voltage reading N to G is not a true voltage.
Should I disconnect all leggs at the panel, just disconnect hots and leave neutral and ground bonded?
attached, post and clean power, and honda sch.
Thank you