mtnelect
HVAC & Electrical Contractor
- Southern California
- Contractor, C10 & C20 - Semi Retired
This concerns a 100 amp electrical service replacement for an older home were the electrical service is in the back yard and the water service is in the front yard. The inspector from a new city wants us to run 60 feet of #6 copper to the water service. We have received an exemption from this requirement from other local jurisdictions in the past. We have filed an appeal with the city, based on the opinion that the higher impedance of the longer run would cause a delay in clearing a fault.
The 2011 NEC has changed the wording from the 2008 NEC, it now appears that connecting to a metal underground water piping system, being used as a grounding electrode is not required to be made within 1.52 m (5 feet) of the point where the underground metal water pipe enters the building. In the 2008 NEC the last sentence stated "shall not be used" which required an exemption in the case of industrial, commercial, and institutional buildings and structures. Another modification was a deletion of the words "grounding electrode system" from the last sentence of 250.52(A)(1) which now means 250.68(C)(1) only applies in the case of an interconnection to other grounding electrodes and even then the wording was changed to "shall be permitted". The main paragraph of 250.68(C) applies to both grounding electrode conductor connections as well as bonding connections to other grounding electrodes, but even then the paragraph used the words "shall be permitted" rather than "shall not be used" which were the words used from the 2008 NEC.