I agree, your utility will NOT like you very much if you are loading up one phase at 3000A... it will unbalance their transformers big time, all the way up the line.Do you have a single 3000 amp single phase load, or do you have multiple single phase loads that would add up to 3000 amps if supplied from single phase only?
A load(s) with that high of amp draw would be something you normally want to balance across all three phases. If that is what you do have you would cut it down to 1732 per phase if divided across all three phases.
If I am on wrong path here please clarify what you are asking.
Confused with 208V, 1 phase calculation. 208V single phase uses two poles. I have a load of 3000A and in the revit panel schedule, showing a value of 2582A at each phase. How is that value calculated?
Even when you use kVA the question comes up (and I think it is the one the OP is asking about) of what to do with line to line loads.And that's why you always work in KVA; KVA does not lie, and it is not distorted by voltage changes. KVA is KVA.
If the panel schedule is totaling amps, it is junk, don't use it.
It sounds like you may be trying to use individual load amps and trying to add them up, when in reality you need to add kVA's and then calculate current.
The NEC does not seem to care about that.Accept it.
It's as GoldDigger said. Divide the kVA between the two buses, i.e. 624kVA@208V ÷ 2 = 312kVA/bus = 2,600A/bus@120VConfused with 208V, 1 phase calculation. 208V single phase uses two poles. I have a load of 3000A and in the revit panel schedule, showing a value of 2582A at each phase. How is that value calculated?