Data Center Generator
NEC User
I'm designing a data center (significant amount of IT loads) with a back-up generator and I'm trying to determine if I should use a 3 pole or 4 pole ATS. Should the fact that the generator will back up sensitive electronic equipment affect my decision?
I always prefer separately derived (4 pole ATS) over non separately derived (3 pole ATS) systems. I can't think of any argument why a non separately derived system would be better. The only time I would implement one is if it's part of an existing system that only has 3 pole ATSs.
Presuming that the only equipment actually powered by the generator is a UPS, lights, and HVAC, I'm not sure it matters much at all, power-quality-wise. You may prefer wiring the generator as an SDS for other reasons. I generally see them as non-SDS with 3-pole ATS.
Interesting opinion.
Why would there be a benefit to opening the neutral?
If this is a large 480V load / generator, I typically leave the neutral at the alternator with a neutral to ground bond, then don't need to worry about carrying a neutral down stream. The small amount of 277V loads get a 480 - 480/277V transformer.
This is the same thing we are doing on a large data center we are currently constructing.