Help! I responded to a service call about HVAC system controls not working and the problem seems to be MUCH BIGGER. I have attached a diagram of the service and a document detailing everything I found, but here is the problem in brief...
200A 240VAC standard residential service in the US.
L1-to-L2 read 247 VAC -- ok
L1-to-neutral bus on left read 123 VAC -- ok
L1-to-neutral bus on right read 247 VAC
hmy:
L2-to-neutral bus on left read 123 VAC -- ok
L2-to-neutral bus on right read 101 mVAC, i.e. essentially no potential
hmy:
Neutral left-to-neutral right read 123 VAC
hmy: As an odd test, I literally connected a drop light to the two neutral busses with alligator clip leads and the light went on! There is no continuity between the two neutral busses (O.L. for Ohm reading on multimeter).
Point 1) Yes I tried a completely different Fluke multimeter and got same results.
Point 2) The above anomaly (at least as far as the voltages go, not sure about resistance reading) disappeared when a breaker to a 100 A sub-panel was turned off.
Point 3) Moving to the sub-panel, there are 3 single pole breakers that cause the anomaly when turned on (with a load tying to energize) all of them fed from the L2 side.
Point 4) Everything including HVAC worked fine in this house for many years until recent problem became evident with HVAC controls. No physical changes were made to the electric power system nor any circuits that homeowner is aware of. I'm not saying everything in this house was electrically "correct", I'm just pointing out that everything worked.
I know there is a lot to read in the attachments, so I express gratitude in advance for anyone willing to wade through it all.:happyyes:
200A 240VAC standard residential service in the US.
L1-to-L2 read 247 VAC -- ok
L1-to-neutral bus on left read 123 VAC -- ok
L1-to-neutral bus on right read 247 VAC
L2-to-neutral bus on left read 123 VAC -- ok
L2-to-neutral bus on right read 101 mVAC, i.e. essentially no potential
Neutral left-to-neutral right read 123 VAC
Point 1) Yes I tried a completely different Fluke multimeter and got same results.
Point 2) The above anomaly (at least as far as the voltages go, not sure about resistance reading) disappeared when a breaker to a 100 A sub-panel was turned off.
Point 3) Moving to the sub-panel, there are 3 single pole breakers that cause the anomaly when turned on (with a load tying to energize) all of them fed from the L2 side.
Point 4) Everything including HVAC worked fine in this house for many years until recent problem became evident with HVAC controls. No physical changes were made to the electric power system nor any circuits that homeowner is aware of. I'm not saying everything in this house was electrically "correct", I'm just pointing out that everything worked.
I know there is a lot to read in the attachments, so I express gratitude in advance for anyone willing to wade through it all.:happyyes: