Sizing Feeder Breaker
I am trying to size a feeder breaker that will feed (3) 25HP, 35 FLA motors. Each motor will be controlled by a drive. One of the motors and drives will not be used and will be installed as an online spare incase of a breakdown. Each drive contains a 50A Circuit Breaker on the Line Side, so one of these will be open and locked until needed. So for sizing this feeder breaker, should I size it using only two motors since they will be the only two pulling load on the circuit or should I size using all three motors?
I will be using NEC 430.24 to size my feeder breaker:
Option 1- Two Motors
(35*1.25)+35= 78.75A (use an 80A Feeder Breaker)
Option 2- Three Motors
(35*1.25)+35+35= 113.75 (Use a 125A Feeder Breaker)
I would size the feeder using the specs of the drives.
Note 430.24 is for conductor sizing... not breaker rating determination.
For breaker rating determination, see 430.53.
And if by "drive" you mean VFD, see Article 430, Part X. Adjustable-Speed Drive Systems to determine if there are any nuances...