How many of you guys have inspectors that when inspecting a new home will look at nameplate on the range?
proper receptacle (50 amp 4 wire vs 3 wire) and proper overcurrent protection on the conductors used (40 or 50 amps depending on conductors used) is all I ever see being looked for. Some may be surprised how big of a range can be put on a 40 amp circuit and never trip a breaker. I can not recall ever having a service call for overload on a range circuit unless something was wrong. Table 220.55 sees the real world load conditions in this way, you can have up to a 12kW range and only need to figure it at 8kW for a single range installation, that is only 2/3 the capacity of the range. The notes say for over 12 kW to 27kW you only have to increase that value by 5%.