multiwire circuit 2 pole breaker, any alternate means for using breaker ties?
howardrichman
I'm wiring a 120V septic pump conduits into panel room, and bringing in the low V alarm wiring isolated. I need an outlet for the alarm, and considered a 3 wire multi circuit feeding thru j-box for the pump, and other for the outlet from a close by panel. I know normally I'de need a 2 pole breaker or 2 breaker tye handled, but obviously I cant have the outlet for the alarm go out w/ the pump if a short circuit occurs. Is the only way to do the extra work to install a separate outlet for the alarm?
HR...
As long as they are sharing a common neutral there must be either a 2p breaker or approved handle tie. I don't see any other options other than running an additional neutral.
Well; I'm using a 12/4 w/gnd. mc cable. Could I use the extra (blue) conductor as a 2nd neutral in the same J-box ?
Thanks for reply;
HR...
No...
It can't be blue and the use of white tape, paint, or other methods of identification isn't permitted for grounded (Neutral) conductors 6 AWG or smaller 200.6(A)
True but not without exception. See 200.6(E) Exception No. 1... but the qualifier is the kicker. Has to be a supervised facility, per se.
No...
200.6 Means of Identifying Grounded
Conductors
(A) Sizes 6 AWG or Smaller. An insulated grounded con-
ductor of 6 AWG or smaller shall be identified by one of the
following means:
(1) A continuous white outer finish.
(2) A continuous gray outer finish.
(3) Three continuous white stripes along the conductor’s
entire length on other than green insulation.
(4) Wires that have their outer covering finished to show a
white or gray color but have colored tracer threads in
the braid identifying the source of manufacture shall be
considered as meeting the provisions of this section.
I have the '11, maybe '14 cleared it up some more. The code is a bit wordy but I think a white with a coloured tracer is ok.
Conductors
following means:
But in his application he does not have colored tracer threads in the braid identifying the source of manufacture.
For MC cable would need to use a 12-2-2 cable (if you can find one), then you would likely have two white conductors with tracers of some sort to identify which ungrounded conductors to pair them with.
I can find it, I call it 12/4 (white, black, red, blue & green) it works great. :cool:
I'm sure it works, but still is only one white conductor.
NM cable is made and called 12-2-2 that has two white conductors - each with a tracer or other ID - I'd guess that they do make MC cable like that as well, but not sure how readily available it may be.
If code let us just re-identify say the blue then availability of 12-2-2 would likely shrink and people would just buy 12-4.
Though I also think the bigger driving force behind demand for 12-2-2 NM was AFCI requirements and the need for separate neutral conductors where people were once using MWBC's.
Try AFC from my area http://www.afcweb.com/
Up to 12-2-2-2-2 if you want identified whites for each hot. http://www.afcweb.com/wp-content/uploads/2015/06/home-run-cable.pdf
Or 12-2 through 10-2-2-2-2-2-2 here http://www.afcweb.com/wp-content/uploads/2015/06/mc-metal-clad-mc-plus.pdf
We use a lot of AFC cable, we can get it to match typical modular furniture feed colors making connections a breeze.
However, most supply houses around me will have 12/4 in stock vs next day for 12-2-2 etc.