mshields
- Boston, MA
I've got a 5MVA substation consisting of ALL pad mounted components and full height Eaton 5kV vacuum switchgear in a walk in enclosure. As none of the components have live parts, we'd have been within code requirements not to have a fence around it. We did nevertheless call for a galvanized steel chain link fence, specifically calling for galvanized as opposed to vinyl coated such that it could be properly grounded.
What was installed was a vinyl coated. The post are grounded and tied into the ground grid but of course the chain link itself is isolated from that grounding by virtue of it's coating. I thought at first glance that the exception under 250.190 might provide an out for having to ground this. But then I see that a requirement is that the fence not be grounded. This fence is grounded to the same ground grid that grounds all of the equipment.
My opinion is that it is therefore a code violation. So a) do you agree and b) would ungrounding the fence make it code compliant? Fence posts would still be grounded via their foundation but grounding would be independent of the grounding network for the substation.
Thanks,
Mike
Thanks,
Mike