I had a question related to ground fault requirements when there is no main breaker with service entrance equipment used in conjunction with the Six Disconnect Rule. The current design uses a 13.8kV main breaker which feeds a 13.8-480V transformer which in turn feeds a switchboard with (4) feeder breakers rated for 1000A trip. For Arc Flash mitigation purposes there will be a set of CT's on the Switchboard main bus that will be wired back to a trip unit located at the MV breaker in order to quickly trip the MV breaker in the event of a fault.
I know for typical services 1000A or greater ground fault protection is required. I'm assuming with no main then the ground fault protection would be required on the 1000A feeders since they are rated 1000A. Is this correct?
These feeders do not have ground fault protection so I was curious if the CT's located on the Switchboard main breaker used to sense fault current at the main bus and trip the high side breaker, could be considered the required ground fault protective device in this case?