Hello,
My question / concern is this: I understand derating, but still have seen an application several times recently that has me puzzled.
The scenario is that large conduits, typically 3" are being used as like a "branch-feeder" for Data Racks in some areas. Other areas to serve Office workstations.
The run will typically be under 100' and hit 3 larger jboxes w/sealtight whips with one receptacle.
So there would be a potential of gradually adding conductors over time to this "branch-feeder" and you could end up with over 41 CCC's on a 42 circuit panel-knocking the amp value down to 35% of what started out at 50%, a #10 was good for 20A, now only 14A and still on a 20A breaker.
I need to explain to those who are "uneducated" in codeology or theory why we don't run a 3" with 50+ CCC's in it.
Any suggestions on how to walk someone who is basically clueless through less, and yes they are in management.
Help.
My question / concern is this: I understand derating, but still have seen an application several times recently that has me puzzled.
The scenario is that large conduits, typically 3" are being used as like a "branch-feeder" for Data Racks in some areas. Other areas to serve Office workstations.
The run will typically be under 100' and hit 3 larger jboxes w/sealtight whips with one receptacle.
So there would be a potential of gradually adding conductors over time to this "branch-feeder" and you could end up with over 41 CCC's on a 42 circuit panel-knocking the amp value down to 35% of what started out at 50%, a #10 was good for 20A, now only 14A and still on a 20A breaker.
I need to explain to those who are "uneducated" in codeology or theory why we don't run a 3" with 50+ CCC's in it.
Any suggestions on how to walk someone who is basically clueless through less, and yes they are in management.
Help.