emt used as equipment ground
slc410
Madison wi
When using emt as the equipment ground is there a size limitation on the ungrounded wire that would require you to run a supplemental egc? In other words no matter what size ungrounded wire, can the emt can still be used? Code article if possible?
358.60
What more do you need?
No, but there may be a length limitation.
You walk into an older factory on the East Coast or along the Detroit River and you see miles of conduit run all without an equipment ground. So the part about limiting length is more or less a theoretical conversation, not a reality. Conduit used as ground has been shown in testing to be a superior way to deal with returning fault current to it's source than using a copper conductor run inside the conduit.
I always thought that the emt was a better equipment grounding conductor than the conductor sized for the situation. I cannot imagine at what point a conductor would be better. Eventually the conductor would have to be so large that the emt would also have to be increased.
A better way to state this is to say that if the conduit run is so long the conduit itself is not able to handle enough current to create an effective ground fault return path, than by that same length the circuit wiring contained within has suffered enough voltage drop from extended length to be virtually worthless. So in conclusion----
Length limitation for metal conduit systems is determined by voltage drop on conductors rather than by the fault ability of the conduit itself.
Exactly.It's an interesting hypothetical to bear in mind, but practically speaking the odds of this being a problem are very low.
Based on the paper Infinity posted, any equipment ground would become ineffective after 400 feet, conduit or cable, if not upsized for voltage drop.
It seems uncommon that someone would be powering a load at such long distances with zero VD consideration.
Yes, I've observed the same thing. Once upon a time, it was standard practice not to run an EGC in metal raceway just about nationwide. I'm not sure what turned the corner on that issue, but maybe electricians took their time back then and did better work. Either that, copper.org's marketing campaign was very effective.
Exactly.It's an interesting hypothetical to bear in mind, but practically speaking the odds of this being a problem are very low.Based on the paper Infinity posted, any equipment ground would become ineffective after 400 feet, conduit or cable, if not upsized for voltage drop.It seems uncommon that someone would be powering a load at such long distances with zero VD consideration.
There's also the high probability that in a commercial or industrial setting, the raceway is mounted to metal (rack, building structure, steel frame, etc) about a jillion times back to the source, thus vastly increasing its current carrying capability.
Absolutely, there will almost always be parallel paths.
But I will concede that when designing a circuit the electrician can't depend on that, so it should be wired for a worst-case scenario.
As a general rule no you can't depend on that.
Some applications however you have steel everywhere, no matter how hard you try to increase resistance to ground - you will have a hard time if that is your intent. Worst case still generally means if the ungrounded conductors fit inside the raceway - it has lower resistance then the wire type EGC you otherwise would pull in that raceway. If you have to upsize conductors for VD, there is a good chance you also need to upsize raceway.
For anybody interested you can download the GEMI software HERE
Roger
SHHH........
I'm surprised to see that EMT has a longer length limit than RMC for a given trade size/OCPD combination. Intuitively I would think that RMC with threaded couplings would have the best grounding performance of any steel raceway.
What blows my mind is the thousands of irrigation services around here with runs of 1300-1500 feet or even more that are usually aluminum conductor in PVC conduit.
The tables there only say aluminum conductors are effective (per the standards stated) up to maybe 100-150 feet in the sizes most commonly encountered:eek:
But I can agree from some personal experiences that not enough fault current flows to blow fuses in a lot of these applications - quite often you just find a lot of arc damage at the fault location but fuse never blows.