What is the purpose of equipment grounding for UNGROUNDED AND HIGH RESISTANCE GROUNDED SYSTEM on a single line to ground fault?
What is the purpose of equipment grounding for UNGROUNDED AND HIGH RESISTANCE GROUNDED SYSTEM on a single line to ground fault?
Does it mean that overcurrent protective device are allowed NOT TO CLEAR THE FAULT IMMEDIATELY? Isn't this dangerous?![]()
In a Ungrounded or HRG system, yes.Does it mean that overcurrent protective device are allowed NOT TO CLEAR THE FAULT IMMEDIATELY?
Not if everything is done properly.Isn't this dangerous?![]()
Yes.Does it mean that if the equipment is properly grounded and bonded in UNGROUNDED AND HIGH RESISTANCE GROUNDED SYSTEM, it is SAFE even if the over-current protective device will not clear the fault?
Yes.Does it mean that EQUIPMENT GROUNDING and BONDING PURPOSE is not COMPLETELY THE SAME in SOLIDLY GROUNDED SYSTEM as compared with UNGROUNDED AND HIGH RESISTANCE GROUNDED SYSTEM on a single line to ground fault?:?:lol:
250.166How should grounding conductor (green or bare) should be sized if the SYSTEM GROUNDING is UNGROUNDED and High resistance grounded? Can it be sized with minimum since maximum current will only be 10 amps?:?:?
250.122?250.166
Yes.250.122?
250.122 applies to all equipment grounding conductors.Are this tables applicable only for SOLIDLY GROUNDED SYSTEM where maximum current is the highest on a single line to ground fault?
Maximum current for line-to-ground fault in HRG and UNGROUNDED is only 10Amps. Should there be an exemption?? If the system is UNGROUNDED or HRG?
Are you sure you understood? I just explained when/why the EGC may carry much more then 10 amps.Ok I understand why we should still follow the table on minimum size of grounding conductor in 250.122 in UNGROUNDED AND HRG.:roll: