You can connect all the EGCs together within the box, ie use a wire nut or you can connect them to the box, ie using grounding screws or clips.
Regardless of either method, or a combination of both, the box must be bonded.
In the first sentence above the "OR" gives you an option not to have to connect to the box.
What rule requires the 2nd sentence above if you run EMT and pull a EGC in the conduit?
That's my dilema with this.
JAP>
In the first sentence above the "OR" gives you an option not to have to connect to the box.
What rule requires the 2nd sentence above if you run EMT and pull a EGC in the conduit?
That's my dilema with this.
JAP>
If the sentence said "and" wouldn't that require you to connect to a non-metallic box?
You are ignoring the part of the sentence that says "in accordance with 250.148(A) through (E)."
See 240.148(C).
You are ignoring the part of the sentence that says "in accordance with 250.148(A) through (E)."
And perhaps the name off the section itself.
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes. Where circuit conduc-tors are spliced within a box, or terminated on equipment within or supported by a box, any equipment grounding con-ductor(s) associated with those circuit conductors shall be con-nected within the box or to the box with devices suitable for the use in accordance with 250.148(A) through (E).
Exception: The equipment grounding conductor permitted in 250.146(D) shall not be required to be connected to the other equipment grounding conductors or to the box.
It's still worded goofy.
They should have left the "within the box or" out of the sentence and added a sentence with some clarification.
........any equipment grounding con-ductor(s) associated with those circuit conductors shall be connected to the box with devices suitable for use...........
Where boxes used are non-conductive, the EGC's shall be connected within the box.
Just sayin,,,,
JAP>
That's how I understand it, too.If I understand 250.148 correctly, the ground(s) do not have to be spliced nor bonded to the box unless the circuit conductors are spliced or terminated to a device in the box. If all of the conductors are pulled straight through the box without terminating or splicing, no connection to the box or splicing is required.