Happy Thanksgiving to you all. I appreciate you taking the time to read my post. I am a residential building inspector and have been writing up NM in conduit for a while now and just received some push back from an unhappy home seller who lost a deal to my report. Basically here is the scenario - 1999 build house with basement that was finished by the homeowner in 1999 as well. Basement NOT done with permit OR licensed electrician. Many defects found (open splices, junction boxes without covers, loose runs of wire not secured within 12" of the termination, etc.) and the one issue they raised with me is how NM was allowed in conduit under the 1999 NEC.
For clarity, I understand NM in conduit to be an issue under three specific chapters:
For clarity, I understand NM in conduit to be an issue under three specific chapters:
334.12(B)(4) and 300.5(B) and 300.9 - I understand the issue to be a conduit "system" is a piece of conduit >/= 18" in length, a nipple is <17" in length - correct? So, any conduit system is by default a "wet location" which prohibits the use of NM. Even indoors correct? When was NM wire prohibited from use inside conduit? Thank you for your help!