I have a 4*4 deep 3/4" threaded hole cast aluminum bell box 3r rated that was connected to the solar rails that are bonded all together using the small clips that are provided in box to connect it to the solar rails using a stainless steel tek screw.
I failed inspection because I did not put a jumper from the the bell box and splice together with EGC coming into the box from the rails.
The conduit from the bell box is bonded at the inverter. And at the bell box since we used a rain tight emt connector and used channel locks to connect to box via threading.
I do not feel it is necessary to put a Bonding jumper for the box, and splice into egc from rails because box is bonded to rails even if there are splices in the the box.
The conductors in the conduit and bell box is also ungrounded since it is a TL inverter with ground fault protection and complies with 690.35.
It is bonded for lighting and since it already has ground fault protection that is insanely sensitive for dc site built into inverter.
So do I need a jumper inside box or are the aluminum 3r bell boxes sold at all electric distribution companies in the country bonded to rails?
Sent from my HTC One_M8 using Tapatalk