Electrical Lead
Electrical Lead
Our system consists of a 25KVA primary and we break that down into 13 subs that are all 480V on the secondary. Only two of those systems are grounded, pulling XO to ground at transformer. The other 11 subs are ungrounded where XO is floating and not pulled to ground any where. We run EGC from metal to metal, but only pull down XO at a lighting transformer or isolation transformer when we have to limit the voltage to ground for equipment reasons. The new system going in does not have a neutral buss in the switchgear, but does have a 2500A main. Contractor pulled 4 wire in and hooked both the white neutrals and the grounds to the same EGC buss at switchgear. What I think will happen now is that if we get a fault on either the primary or any secondary on the plant, this type of connection will create a ground loop and cause all kinds of stray voltages and currents to burn up a lot of stuff. I believe contractor should leave the neutrals off from switchgear ground buss and tie neutral down at transformer which would leave the new system ungrounded.