Acxpert
- San Francisco, CA USA
Looking for some guidance on an MCC sizing/capacity issue. Here is the situation:
There is an existing 600 amp MCC with several loads, all HVAC units, fans and pumps. The MCC itself is fed by a 600 A breaker and (2) #400 wires per phase.
The plan is to remove most of the equipment and replace it with 2 large package units. It appears that the panel was overloaded already, per the loads below:
Electrician is telling me that the max load we can put on the MCC is 80% or 480 amps. Is this correct?
I was hoping we can feed our new AC units out of the MCC and re-feed the smaller loads that need to remain from elsewhere. Any thoughts?
Thanks!
| Existing Equipment | HP | MCA | Fuse size | Comments |
| AH-1 | 40 | 80 | To be demo'd | |
| AH-2 | 40 | 80 | To be demo'd | |
| EF-1 | 10 | 30 | To be demo'd | |
| EF-2 | 10 | 30 | To be demo'd | |
| PD-1 | 3 | 8 | To remain | |
| PD-2 | 3 | 8 | To remain | |
| ACP-1 | 3 | 8 | Abandoned | |
| CU-1 | 117 | 150 | To be demo'd | |
| CU-2 | 117 | 150 | To be demo'd | |
| CU-3 | 117 | 150 | To be demo'd | |
| CU-4 | 117 | 150 | To be demo'd | |
| AC-1 | 41 | 60 | To remain |
Thanks!