underfloor raceways in industrial facility

Status
Not open for further replies.
visited a warehouse that has trenches built into the concrete floor with 1/2" steel cover plates as covers. A forklift managed to move a plate as it rolled over it and nailed a 480V conductor laying in the trench. Is this trench considered a raceway as other conduits run through here as well as other unprotected conductors feeding other equipment?

:?
 
With the cover just laid in place rather than fastened, I would not call it a raceway. Certainly not a listed or approved raceway. More like a covered cable tray but not that either.
Probably not acceptable to put non- cable wire types there without a raceway.
Events prove it was not well protected against physical damage.
 
That's how our plant does things, we have trenches cut in the floor and then inset with steel. It is not a raceway. We use these trenches to get air, gas, power, welding grounds, and hydraulics from point A to point B. I wouldn't consider inside the trench susceptible to physical damage but we do it all in rigid regardless.


Sent from my iPhone using Tapatalk
 