Santa shocked Me
jap
Went to plug in 6' tall roughly 3' wide Santa last night which I welded togehter out of 5/16 round rod about 5 years ago and outlined with white and red chrismas lights propped up with a 4' piece of 3/4" emt I drive into the ground behind him.
He's been doing good for all this time yet the light string has become brittle and frail over the years.
Since hes only lit up for about 2 weeks out of the year I've been putting off upgrading the over 300 lights and time it would take to re-string him.
The extension cord I made years ago was simply a 50' rubber cord I had in the truck with a regular receptacle in a handy box on the end of it (I dont want to hear it...) but it is plugged into my outside GFI receptacle which tests good.
When I went to plug him in last night in the dark, I was kneeling on the wet ground next to him and one of the wires of the 2 wire stringer was broken awey from the plug (without my knowledge of course) as soon as I went to plug it in, I became the return path from the stringer of lights and the metal handy box or so I think.
There for a while, I was the santa that was lit up standing behind the sled with my 3 deer herd trying to get my jaws to unlock to sing Silent Night all the time wondering why my GFI wasnt tripping.
Still not sure.
JAP>
Still not sure.
JAP>
HO HO HO:D
Still not sure.
JAP>
Isn't it ironic how LONG 3/10ths of a second can be?
Remember a class A gfci trips between 3-5 ma. You may still have gotten a nice 2.5 ma jolt!
The standard says they are not permitted to trip below 4mA, may trip between 4 and 6mA, and must trip above 6mA.
The maximum permitted time to trip in seconds is equal to the quantity (20/fault current in milliamps) raised to the 1.43 power. The application of this formula would permit a 7.26 second trip time for a 5 mA ground fault.
It is my understanding that most devices trip in about 1/4 of a second no matter what the ground fault current is, but the standard permits a much longer clearing time for low current faults.
Everyone that complains about GFI's should grab onto an energized Santa and let thier bells get jingled for a little while.... maybe then they'd grow to appreciate them a little more... the ones that actually trip when needed that is...
JAP>
JAP>
Many don't realize that 4-6 mA still gives you one hell of a jolt. This amount needs to flow before it will trip. Many also think GFCI's prevent shock, though they do eliminate them before they happen quite often, current must flow before they activate, if you are in the path you will feel it.
They limit the duration of shock.
They (hopefully) eliminate electrocution.
Still not sure.
JAP>
So, when you tried to light up Santa, he lit you up instead? :D
This happened to my boss. He got in series with a ground fault on a GFCI protected circuit and he felt it big time before it tripped.
JAP>
If you are the fault path a GFCI will not prevent you from getting a heck of a shock till it has a chance to respond and open the circuit.
They can only limit the time you are getting the shock, they can't limit the intensity of the shock.
True.
One tends to get used to the almost instantaneous quick reaction trip, that most of us witness when troubleshooting a GFI Tripping when something is wrong.
Not so much the case when your actually the path.
JAP>
Most of the time we are protected because something else has taken the fault current and tripped the device before we are part of the path, which is why there aren't too many shock incidents when GFCI protection is utilized, but there is still those occasional times when first fault current is through a person.
The part you didn't want to hear about possibly made it worse then it would have been had you not been holding a grounded object in one hand while contacting the damaged cord in the other hand, though I guess you said you were kneeling on wet ground so maybe would have gotten a good hit anyway.
This is what I try to explain to customers when I visit and notice the ground prongs missing or they are using two wire adapters.
The GFCIs may work without that 3rd wire but you have replaced it during a fault and you WILL feel it however long or short of time it takes to operate. I hope your heart is healthy. Have you tested them lately?
With the wire broke loose from the plug, my finger was actually in series with the neutral return.
Not sure if the GFI would have ever tripped depending on how much current I was sending into the dirt.
JAP>